Old 06-08-2015, 04:23 PM
  #16  
Ducman82
 
Ducman82's Avatar
 
Join Date: Nov 2009
Location: Marysville WA
Posts: 6,983
Received 18 Likes on 11 Posts
Default

greg told me to let it run for an hour or 2. close the vac pump line and let it sit overnight to see if the needles drop, indicating a leak
Old 06-08-2015, 04:43 PM
  #17  
Rob Edwards
Archive Gatekeeper
Rennlist Member
 
Rob Edwards's Avatar
 
Join Date: Sep 2002
Location: Irvine, CA
Posts: 17,615
Received 2,792 Likes on 1,360 Posts
Default

I finally got around to buying a short adapter hose so I can run my micron gauge in line with my Robinair pump- Next time I have a car to evacuate I will collect some data on how deep a vacuum it'll generate, how fast.
Old 06-08-2015, 05:07 PM
  #18  
Bilal928S4
Drifting
 
Bilal928S4's Avatar
 
Join Date: Apr 2011
Location: New Canaan, CT
Posts: 2,871
Likes: 0
Received 15 Likes on 9 Posts
Default

What I have found is that when you shut off the pump, it has to be disconnected from the gauges, otherwise the hose to the gauge will get filled with the vacuum pump oil. Even if the gauges are closed, the hose is still under a negative and will suck the vacuum pump oil up.
Old 06-08-2015, 05:23 PM
  #19  
Rob Edwards
Archive Gatekeeper
Rennlist Member
 
Rob Edwards's Avatar
 
Join Date: Sep 2002
Location: Irvine, CA
Posts: 17,615
Received 2,792 Likes on 1,360 Posts
Default

My Robinair has a lever that switches between the vacuum hose connection and atmospheric so you can 'break' the vacuum to the pump before turning it off, without affecting vacuum in the hoses. Or you could just close the valves on the gauges and loosen the connecting hose at the pump inlet before turning it off.

The Robinair pump (#15600) was $202 on Ebay a few years back. Incrementally more than the HF 2-stage, but built like a tank.
Old 06-09-2015, 12:51 PM
  #20  
dr bob
Chronic Tool Dropper
Lifetime Rennlist
Member
 
dr bob's Avatar
 
Join Date: Oct 2001
Location: Bend, Oregon
Posts: 20,506
Received 549 Likes on 412 Posts
Default

And of course a reminder that the 'holds vacuum' test is a looky for BIG mistakes. The fittings on the car are o-ring sealed, so vacuum actually draws things together tighter, often sealing small leaks in the process. If you are seriously looking for leaks, pressurize with dry nitrogen and start the search with soapy water at every connection, looking for bubbles. Then evacuate overnight and charge just until pressure is a bit positive relative to atmosphere, search again with electronic sniffer. If still no leaks, add the rest of the charge and sniff/soap spray again. If still no leaks it's OK to start the engine and drive.
Old 06-09-2015, 01:55 PM
  #21  
Kevin in Atlanta
Rennlist Member
Thread Starter
 
Kevin in Atlanta's Avatar
 
Join Date: May 2002
Location: Roswell, GA
Posts: 8,195
Received 823 Likes on 497 Posts
Default

Originally Posted by dr bob
And of course a reminder that the 'holds vacuum' test is a looky for BIG mistakes. The fittings on the car are o-ring sealed, so vacuum actually draws things together tighter, often sealing small leaks in the process. If you are seriously looking for leaks, pressurize with dry nitrogen and start the search with soapy water at every connection, looking for bubbles. Then evacuate overnight and charge just until pressure is a bit positive relative to atmosphere, search again with electronic sniffer. If still no leaks, add the rest of the charge and sniff/soap spray again. If still no leaks it's OK to start the engine and drive.
Which is why I liked the GAST - it does pressurization as well. It was instrumental in finding a gross leak on my 87. I know it is not nitrogen , but it was sufficient.
Old 06-09-2015, 04:15 PM
  #22  
bureau13
Rennlist Member
 
bureau13's Avatar
 
Join Date: May 2014
Location: South Florida
Posts: 3,488
Received 57 Likes on 43 Posts
Default

Tell me more about this....what gas did you pressurize the system with? This is exactly where I stand...it won't hold a vacuum, so I know I have a big leak in something I did, but I have no ability (at least yet) to pressurize with anything.
Old 06-09-2015, 04:29 PM
  #23  
Ducman82
 
Ducman82's Avatar
 
Join Date: Nov 2009
Location: Marysville WA
Posts: 6,983
Received 18 Likes on 11 Posts
Default

so when i did my system (just did), i had resigned my self to that if it would not hold vacuum, would be to re do all the connections. my main concern was the expansion valve o rings. so i made SUPER they had clean seats and the connections had good clean threads. my last "system" had a nice leak due to a chewed up o-ring on one of the compressor connections. it may be worth it to add dye and fill the system up, look for a leak, drain, fix and re charge.
Old 06-09-2015, 04:36 PM
  #24  
bureau13
Rennlist Member
 
bureau13's Avatar
 
Join Date: May 2014
Location: South Florida
Posts: 3,488
Received 57 Likes on 43 Posts
Default

My system is still R12....Any harm in using R134a w/ dye, just to leak-check?

I was really thinking I could find someone to pressurize with nitrogen and find the leak, but haven't had a chance yet.
Old 06-09-2015, 06:43 PM
  #25  
dr bob
Chronic Tool Dropper
Lifetime Rennlist
Member
 
dr bob's Avatar
 
Join Date: Oct 2001
Location: Bend, Oregon
Posts: 20,506
Received 549 Likes on 412 Posts
Default

So the deal with pressurizing with nitrogen is that it's DRY, so you aren't adding moisture to whatever is in there already. You can use almost any dry compressed gas, and nitrigen happens to be the cheapest. Next on the list is probably CO2.

Using the little Gast 'pump' to pressurize the system for leak-check isn't a great idea. Ditto using air from your home compressor, since both have compressed moisture in with the compressed air.

If you have a nearby tire store that offers dry nitrogen fills, you might try having them fill your portable tire-fill tank. But the tank already has moisture in it and no good way to get it out short of a good vacuum pump overnight with the tank warmed to coax the water out as vapor. Can you see how this all forms a big logistics circle?
Old 06-10-2015, 01:49 AM
  #26  
jpitman2
Rennlist Member
 
jpitman2's Avatar
 
Join Date: Dec 2002
Location: Australia
Posts: 5,283
Received 49 Likes on 46 Posts
Default

Mate of mine used an old fridge pump to make a vacuum forming unit for moulding fibre glass. He left it running a bit too long and it crushed the article flat.
jp 83 Euro S AT 56k
Old 06-10-2015, 08:18 AM
  #27  
harveyf
Rennlist Member
 
harveyf's Avatar
 
Join Date: Aug 2009
Location: New Hill, NC
Posts: 2,319
Received 458 Likes on 328 Posts
Default

Easy for me cause I have a MIG welder and a TIG welder, both of which come with bottles of gas, but I used a couple of fittings to introduce the MIG welder gas into the system. Pressurized it to about 90 psi.

In answer to the question about using R134 in a R12 system for testing, I think it was AirTek who suggested this approach in another thread. That is what I did. Of course, if you are going the R12 route (which I did) you'll want to re-evacuate the system to get all of the R134 out. I also used a soap solution. The only significant leak I found was at one of the Schrader valves.
Old 06-10-2015, 11:33 AM
  #28  
dr bob
Chronic Tool Dropper
Lifetime Rennlist
Member
 
dr bob's Avatar
 
Join Date: Oct 2001
Location: Bend, Oregon
Posts: 20,506
Received 549 Likes on 412 Posts
Default

Brings up a good point -- The o-rings at the Schraeder valves are old black crispy bits. When replacing o-rings in the rest of the system, the Schraeder valves need to be replaced too, with correct refrigerant-rated valves of course. With the green HNBR o-rings in them. For my S4 IIRC there are six total Schraeder valves to replace. The two obvious ones at the service ports on the car, one each under the pressure transducer and the low-pressure safety switch, and then the two on the compressor manifold.

When I swapped to R-134a fifteen years ago, I ended up removing the two from the service ports so the adapters would work correctly. The adapters had little depressor tabs on the female sides to open the Schraeder valves, but they ended up just bending the pins over. Since each adapter has its own Schraeder valve, it was an easy choice to just remove the one in the port underneath.

And for those playing along and perhaps not familiar, the charge hoses used between the manifold and the port on the car has a depressor in one end of each hose (red and blue). Make Sure that you have the depressor in the 'car' end so the valve is actually open, else the valve will stay closed until you put enough pressure on it from outside to push it open. You can preven the system from evacuating, and make charging a real chore if you forget this detail.

The depressors and seals on the hose ends are renewable parts. Seals particularly are an annual replace item if you use the gauges regularly. The depressors fall out when you aren't looking, or get mashed when overtightened on the dummy manifold ports. Hoses ALWAYS get stored with the ends closed.
Old 06-10-2015, 11:44 AM
  #29  
Rob Edwards
Archive Gatekeeper
Rennlist Member
 
Rob Edwards's Avatar
 
Join Date: Sep 2002
Location: Irvine, CA
Posts: 17,615
Received 2,792 Likes on 1,360 Posts
Default

I got an object lesson in this after volunteering to check the A/C in a neighbor's Acura TL. Only 25 psi residual pressure in the system- discovered a leaking low-side Schrader valve, with telltale oil and dirt around the connector. Bought a kit of valve cores and a core tool, replaced both valve cores WIWAIT, evacuated overnight. It held perfectly, so I recharged. Charge on an '04TL is ridiculously small- 540 grams (~$5 worth of r134a). Or maybe the 928 charge is just ridiculously large. Dunno.
Old 06-10-2015, 11:44 AM
  #30  
harveyf
Rennlist Member
 
harveyf's Avatar
 
Join Date: Aug 2009
Location: New Hill, NC
Posts: 2,319
Received 458 Likes on 328 Posts
Default

HTML Code:
 When replacing o-rings in the rest of the system, the Schraeder valves need to be replaced too, with cirrect refrigerant-rated valves of course.
Oh crap Dr. Bob. I replaced mine with some I got from Ace Hardware I'll buy some of the correct ones now so I have them for next time. Any advice on where to get them?