Setting up my Compressor to run off gas generator.

Thread Tools
 
Search this Thread
 
Old 08-01-2014, 07:43 PM
  #1  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default Setting up my Compressor to run off gas generator.

I need help with this. I have moved my 220V compressor to a shop arte that does NOT have a 200v outlet nor will I be allowed to add one. However I do have a gas generator that has a 240V outlet. ( see pic) My issue is the compressor and OLD dryer plug I did use only has 3 wires. The generator has a 4 prong plug set up. From what I am reading...I can forgo NOT using the neutral wire....is that correct?

Here is some 928 content....Pulled dash and pod from Dennis car and will recover along with a pod for another Rennlister.


Cant upload pics for some reason right now...will try again in a few minutes.
Old 08-01-2014, 07:46 PM
  #2  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

Finally got the pix to upload.
Attached Images    
Old 08-01-2014, 07:48 PM
  #3  
Ducman82
 
Ducman82's Avatar
 
Join Date: Nov 2009
Location: Marysville WA
Posts: 6,983
Received 18 Likes on 11 Posts
Default

Yes you can forgo it. I had to so the same thing for my old welder. Welder was 3 wire, was 4 I have a pic some where
Old 08-01-2014, 09:23 PM
  #4  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

Thanks.....I just wanted to make sure. Me and electricity don't mix.
Old 08-01-2014, 09:40 PM
  #5  
dr bob
Chronic Tool Dropper
Lifetime Rennlist
Member
 
dr bob's Avatar
 
Join Date: Oct 2001
Location: Bend, Oregon
Posts: 20,506
Received 547 Likes on 410 Posts
Default

There are potential issues with this only if you sometime decide that you want to split the 240 into two 120 legs. At that point your 'neutral' isn't bonded to ground anywhere, and the voltage on the two 120 legs will vary a lot based on the load imbalance between the legs. That said, there's a very good case for adding a safety ground from the generator frame to a good ground point in your shop. You might be able to connect to the ground that is adjacent to the service panel, or drive a copper ground rod into the soil as close as possible to your generator.

More options: Most 240V induction motors less than maybe five horsepower offer an option for wiring for 120V. Usually there's a diagram on the motor itself that shows the connection options.

Compressor motors present a pretty high starting inrush load to a portable generator, especially 3600 RPM motors trying to start into a partially-charged tank. 200% inrush demand is not uncommon. In a hardwired system the short-term overcurrent is managed by using slow-blow fuses or a thermal breaker with a little lag in it. On the generator, the inrush draws the generator engine speed down with the sudden load increase. In the end you'll typically trip the breaker on the generator and trip the thermal protection on the motor.
Old 08-01-2014, 11:50 PM
  #6  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

Thanks dr Bob....a lot of that is very close to the limits of my electrical knowledge.

This is the compressor I have...just a few years older but the specs are the same.
http://www.harborfreight.com/5-hp-60...sor-93274.html

I will post the generator when I find it. If I remember its a 8500 watt max.

I will do some research on how to properly ground the generator. Its on wheels and will be wheeled outdoors when needed.
Old 08-02-2014, 12:39 AM
  #7  
waynestrutt
Rennlist Member
 
waynestrutt's Avatar
 
Join Date: Sep 2011
Location: Caledon.Ont.
Posts: 237
Received 22 Likes on 11 Posts
Default

If the new place has a breaker panel then you have 240v .If you have 3 wires 2 black one white coming into your panel plus a bare ground simply connect directly to these or put a stove breaker in the panel and connect directly to it. I had the same issue with mine taking it to different residences each job and had adapters to connect to the panel, or to the dryer plug, or the stove plug.
Old 08-02-2014, 01:15 AM
  #8  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

Thanks Wayne...the landlord furnishes the electricity for the shop area. No separate fuse boxes for each unit. He has already stated he does NOT want anyone to run 240 lines so his electric bill is as low as possible. Don't want to "rock the boat" as the shop is a 50' x 50' space with shop lights and water furnished in with the rent. I was renting 2 storage units for my belonging when I moved here in 2009. That was about $100 a month with NO electricity and units so small all I could do was store boxes. Now with the shop space...I can store my stuff and have room to work on cars and bikes year round.
Old 08-02-2014, 11:01 AM
  #9  
depami
Rennlist Member
 
depami's Avatar
 
Join Date: Jul 2009
Location: Cleveland, MN
Posts: 2,832
Received 245 Likes on 130 Posts
Default

That sounds awesome Dean. Post pics of the shop when you get a chance.

If you connect the ground at the compressor to building ground you should be good to move the generator at will. Ignore the neutral (N) on the generator. Just use L1, L2 and GND.

I would leave the compressor on 240 rather than switching to 120.

Name:  4 Prong 240 VAC.jpg
Views: 268
Size:  6.6 KB

Last edited by depami; 08-02-2014 at 11:50 AM.
Old 08-02-2014, 03:18 PM
  #10  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

A very nice place to work.
Attached Images  
Old 08-03-2014, 12:11 AM
  #11  
jeff spahn
Rennlist Member
 
jeff spahn's Avatar
 
Join Date: Nov 2009
Location: Dubuque, IA
Posts: 8,599
Received 400 Likes on 224 Posts
Default

Your 928 steals the show hands down.
Old 08-03-2014, 11:27 PM
  #12  
WICruiser
Burning Brakes
 
WICruiser's Avatar
 
Join Date: May 2005
Location: Chilton Wisconsin
Posts: 1,007
Likes: 0
Received 9 Likes on 5 Posts
Default

Make sure you run the generator away from the building and away from any open doors or windows. Most gasoline generators put out a lot of CO emissions that can be a problem in a hurry in any confined space.
Old 08-04-2014, 12:10 AM
  #13  
Dean_Fuller
Drifting
Thread Starter
 
Dean_Fuller's Avatar
 
Join Date: Feb 2008
Location: Columbus, Mississippi
Posts: 3,029
Received 6 Likes on 5 Posts
Default

Thanks Roger...will do. The generator sits just inside a big overhead door. When in use it will be rolled outside and around the corner.
Old 08-04-2014, 12:15 AM
  #14  
Speedtoys
Rennlist Member
 
Speedtoys's Avatar
 
Join Date: Sep 2010
Location: Boulder Creek, CA
Posts: 13,582
Received 1,034 Likes on 623 Posts
Default

I looked up that Generator..it wants at least a 25A 240v connection to run, with a peak inrush of 40a.

A portable generator isn't gonna do it, without burning something up over time, if it doesn't simply pop itself straight away.

Old 08-04-2014, 02:52 AM
  #15  
Jim Devine
Three Wheelin'
 
Jim Devine's Avatar
 
Join Date: Apr 2010
Location: Sacramento, Ca.
Posts: 1,272
Likes: 0
Received 32 Likes on 22 Posts
Default

Look for something like this- they show up on Craigslist from time to time.

http://www.tractorsupply.com/en/stor...air-compressor
You can feed it to your tank for more capacity.
Or you can probably find a big industrial compressor with a 3 phase motor pretty cheap & convert it to gas powered.
As Dr Bob pointed out the starting load of your compressor is a lot more than the running load.
Not good for the start winding on your motor.
When I was a paint contractor, the airless repair shop got lots of units with burned up motors that
painters tried to run off generators.

Great workshop!